An air volume of 420 m3 room with an air supply rate of 840 m3/h and no losses: what is the air changes per hour (ACH), and does it meet a target of 4–6 ACH?

Prepare for the Bioenvironmental Engineering Exam. Use multiple-choice questions and detailed explanations to study efficiently for your exam and enhance knowledge in environmental safety and engineering.

Multiple Choice

An air volume of 420 m3 room with an air supply rate of 840 m3/h and no losses: what is the air changes per hour (ACH), and does it meet a target of 4–6 ACH?

Explanation:
Air changes per hour measures how many times the room’s air is refreshed in one hour. It is found by dividing the ventilation rate by the room volume. With a supply rate of 840 m3/h and a room volume of 420 m3, and assuming there are no losses, the ACH is 840 ÷ 420 = 2 changes per hour. The target is 4–6 ACH, so an ACH of 2 is below that range and does not meet the target. If there were losses or recirculation, the actual ACH could differ, but under the given conditions the calculation shows 2 ACH and the target is not satisfied.

Air changes per hour measures how many times the room’s air is refreshed in one hour. It is found by dividing the ventilation rate by the room volume. With a supply rate of 840 m3/h and a room volume of 420 m3, and assuming there are no losses, the ACH is 840 ÷ 420 = 2 changes per hour. The target is 4–6 ACH, so an ACH of 2 is below that range and does not meet the target. If there were losses or recirculation, the actual ACH could differ, but under the given conditions the calculation shows 2 ACH and the target is not satisfied.